Setpoint Profiles (for Reflow et al)

Setpoint Profiles (for Reflow et al)

Postby Brett » Sun Apr 15, 2012 4:04 pm

I'vejust posted the new firmware / front-end that allows for setpoint profiles. It's fairly straight-forward, but I thought I would create this thread for Q&A.

the jist:
-The osPID can hold one profile at a time. This is stored in EEPROM and can be executed from the main osPID menu, or from the "profiles" tab on the front-end
-A profile is a sequence of up to 15 steps, made up of RAMP, STEP, and WAIT Commands
-To create / load a profile
1. create a txt file in the "profiles" sub-folder of the front-end application. follow the form laid out in reflow1.txt
2. start the front-end. the profiles folder will be read and you will see your new profile int the "available profiles" list on the profile tab
3. connect to the osPID
4. highlight the desired profile and click "send_profile" the profile will be sent to the osPID and you will be notified of progress / success.
5. at this point you can run the profile either from the main osPID menu (last option) or by clicking "Run_Profile" on the profile tab.

as I said, the profile is stored in the osPID's non-volatile memory, so it will stay on-board after a reset. you will only need to re-load if you wish to change the profile to be run.
User avatar
Brett
Site Admin
 
Posts: 99
Joined: Fri Mar 09, 2012 10:05 pm
Location: Boston

Re: Setpoint Profiles (for Reflow et al)

Postby dchris01 » Mon Apr 23, 2012 10:54 pm

I am a bit confused on the reflow chart to edit for my own profile I have tried to set up my profile but unable to succeed any help is good. This is my profile that I am trying to upload. To reflow profile so I can run from front end.
Time. Temp.
30 sec. 100
60 sec. 150
90 sec. 170
120 sec. 200
130 sec. 217 reflow temp
150 sec. 245
180 sec. 255
200 sec. 210
210 sec. 75
240 sec. -
270 sec. -
dchris01
 
Posts: 17
Joined: Sun Mar 11, 2012 10:18 pm
Location: Ireland

Re: Setpoint Profiles (for Reflow et al)

Postby Brett » Tue Apr 24, 2012 12:35 am

if you would like those hard steps, then the profile file would contain the following:
Code: Select all
[profile name, 7 chars max]
3, 100, 30      //step (3) setpoint to (100) and wait (30) seconds
3, 150, 30      //step (3) setpoint to (150) and wait (30) seconds
3, 170, 30      //step (3) setpoint to (170) and wait (30) seconds
3, 200, 30      //step (3) setpoint to (200) and wait (30) seconds
3, 217, 10      //step (3) setpoint to (217) and wait (10) seconds
3, 245, 20      //step (3) setpoint to (245) and wait (20) seconds
3, 255, 30      //step (3) setpoint to (255) and wait (30) seconds
3, 210, 20      //step (3) setpoint to (210) and wait (20) seconds
3, 75, 10       //step (3) setpoint to (75) and wait (10) seconds


just so we're clear, this will adjust the setpoint of the oven (the green line on the front-end.) the actual oven temperature (the red line) will lag behind and will respond to these changes based on your specific oven, and your tuning parameter values (Kp, Ki, Kd). for a smoother profile, it might be more advantageous to use the available Ramp command instead of so many step commands:

Code: Select all
[profile name, 7 chars max]
3, 100, 0      //step (3) setpoint to (100) and immediately go so the next step
2, 0, 0      //we have no idea where the oven temperature was at the start, so wait (2) until it crosses the setpoint from the previous command (100)
1, 217, 100      //ramp (1) the setpoint to 217 over the next 100 seconds
2,0,0        //because the oven temperature is likely lagging behind the setpoint ramp from the previous step, wait (2) until it actually GETS to 217 before proceeding the next step
1, 245, 20      //ramp (1) the setpoint to 245 over the next 20 seconds
3, 255, 30      //step (3) setpoint to 255 and wait 30 seconds
1, 210, 20      //ramp (1) the setpoint to 210 over the next 20 seconds
3, 75, 30      //step (3) setpoint to 75 and immediately go so the next step
2, 5, 3      //wait (2) for input to be within (5) degrees of the of the last setpoint (75) for (3) seconds before proceeding to the next step (END)


Again, this is specifying the REQUESTED temperature (the PID Setpoint,) not the actual temperature. how well the actual temperature tracks with these request will be based on the oven & tuning parameters.

hope this helps

(updated: when I first wrote this, I accidentally got the red/green designation backwards. whoops)
User avatar
Brett
Site Admin
 
Posts: 99
Joined: Fri Mar 09, 2012 10:05 pm
Location: Boston

Re: Setpoint Profiles (for Reflow et al)

Postby dchris01 » Tue Apr 24, 2012 8:23 pm

This is my first go at running profiles on my Homemade IR station top plate controlling this is step profile.
http://img829.imageshack.us/i/imagehyh.jpg/

http://img843.imageshack.us/i/imagephqn.jpg/
This is ramp profile. I didn't get Autotuning to work to Autotuning at 235.
20oC Temp difference between osPID TC and thermometer TC both where within around 5mm of each other sitting beside chip I was testing for solder liquidous. Still learning about osPID which is a superb gadget if thats what you to call it.
Last edited by dchris01 on Wed Apr 25, 2012 2:26 am, edited 1 time in total.
dchris01
 
Posts: 17
Joined: Sun Mar 11, 2012 10:18 pm
Location: Ireland

Re: Setpoint Profiles (for Reflow et al)

Postby Brett » Wed Apr 25, 2012 12:20 am

@dchris that second picture looks great! (the first one had been removed)

it looks like your temperature is tracking pretty well with the setpoint. I'm not sure how much you would gain by changing the tuning parameters. I know that the cool-down looks slow, but if you look at the output you can see that the PID (correctly) dropped the output to 0 early on. the slow rate of cooling is due to the nature of your system. no set of tuning parameters will make that cool-down happen more quickly.

you must MUST post pictures once you start reflowing!

also, just as a side note, if you could comment on the challenges you had getting to this point I think that would be really helpful. I've been doing this for a long time, and I do my best to make thing accessible to the beginner, but sometimes it's hard to forget what I know. there's no substitute for someone saying "yeah, I was really confused by ____. if you had said ___ it would have made things much easier."
User avatar
Brett
Site Admin
 
Posts: 99
Joined: Fri Mar 09, 2012 10:05 pm
Location: Boston

Re: Setpoint Profiles (for Reflow et al)

Postby dchris01 » Wed Apr 25, 2012 2:27 am

Click on picture again I have it fixed Brett cheers
dchris01
 
Posts: 17
Joined: Sun Mar 11, 2012 10:18 pm
Location: Ireland

Re: Setpoint Profiles (for Reflow et al)

Postby Brett » Wed Apr 25, 2012 10:30 am

@dchris I'm glad you posted that first picture. it's very revealing about the nature of your oven's heating. similar to the cooling thing, I can see that the output is fixed at 100% during the entire heating portion. the heaters can't give any more. so this is as fast as your oven can heat up. no PID in the world can make it go faster.
User avatar
Brett
Site Admin
 
Posts: 99
Joined: Fri Mar 09, 2012 10:05 pm
Location: Boston

Re: Setpoint Profiles (for Reflow et al)

Postby dchris01 » Wed Apr 25, 2012 7:42 pm

I am having problems with loading a profile from pc to ospid. When i select a profile i select send then when it completes i run and it works then say I do another test in 30 mintues time and load another profile the same way, it wont load up and nothing shows on status bar but its running on the ospid but not on pc. This has happen a few times. I would rather use the pc for seeing what is happening rather than looking at ospid it seems to me i am controlling the reflow better. That is my option.
dchris01
 
Posts: 17
Joined: Sun Mar 11, 2012 10:18 pm
Location: Ireland

Re: Setpoint Profiles (for Reflow et al)

Postby dchris01 » Wed Apr 25, 2012 11:12 pm

This was the ramp profile. I changed first Step from 100 to 130 and it did help as you see in picture. Only thing was temp on ospid and tc beside chip was that they were around 30oC of a difference. http://img685.imageshack.us/i/imagedwv.jpg/
This was the step profile 30 min before didn't look good compared to ramp profile.
http://img13.imageshack.us/i/imagetit.jpg/

And here is my setup not a finished project as you see but working and like everything else a lot of testing.

http://img23.imageshack.us/i/imagewjj.jpg/
dchris01
 
Posts: 17
Joined: Sun Mar 11, 2012 10:18 pm
Location: Ireland

Advice on knowing if everything is working

Postby Maddox » Thu Apr 26, 2012 1:47 am

I wired up a toaster oven to ac hot and I know that is working since the 1/2 second oscillation on the relay is flashing the oven light and it is warming up (swiftly) using the sample reflow profile. I *believe* the thermocouple is wired correctly, but I don't can't find any indication that the osPID is reading it, since the sample reflow profile is waiting for the oven to reach 50, and my standalone thermocouple continues to rise over 120 before I killed the run.

Is there a simple thermocouple test that I have missed?

Thanks for any help.
Maddox
 